This past winter my wife bought a 2009 Dodge Charger. Now that she has that car and drives it year round, she's planning on selling her 97 Camaro RS. When the Camaro is gone, this will mean I get the entire shop to myself. One thing that I have always found really annoying in the shop is a post in the middle of the shop. I know it is a load bearing post, but is there anything I can do (that won't cost me a fortune) to get rid of the post. Why do I want to get rid of it....I think that's obvious :unibrow:
Here's a pic of the shop and the post I'm talking about. The beam above the post runs the length of the shop. That beam is two 2x10's screwed together to make one beam. http://i222.photobucket.com/albums/d...9/PICT0090.jpg Here's a couple pics of the attic. I was wondering if I would be able to add more 2x4's to support the roof enough to remove the post. http://i222.photobucket.com/albums/d...9/P1000406.jpg http://i222.photobucket.com/albums/d...9/P1000409.jpg Anyone have any thoughts?? Thanks in advance. |
Looks kind of important. :unibrow:
|
Whats the span and is that beam directly under the ridge? Adding more 2x4's wont do anythig. That beam is more than likely just holding up the cieling joist by looking at the pics. You could or should of had some collar ties on those rafters. You can put a larger beam in to handle the span and load, but lots of work.It would be better to have the bottom of the beam flush with the cieling and burry the rest in the attic if that makes sense. Of course I dont know if the existing footings are large enough or what your roofing or snow loads are in that area. You would need an engineer, maybe from a truss plant, to calc that for you,... or hang a naked girl calander on the post and call it a day.
Also, I think it's time to cash in the cans. |
Bring the beer cans to Washington they're worth a nickel a piece - then hire a proper contractor. :rofl:
|
Seriously - that span would have to have one heck of a beam without the post... You're carrying the roof load - and you have to calculate for a snow load etc.
I put up a "mezzanine" in the shed -- it has a single beam to carry the floor - no roof load - and it runs 16 feet - and it's 8" wide by 19 1/2" thick! |
That beam isn't holding any roof load at all. Its holding the celing joists like WAR noted. First off a double 2x10 beam isnt much at all so the load isnt that great regardless of span. What is the total span of the double 2x10 beam ? The live load in clg joists arent as much as a live load in a floor joist. The clg joist dead load may not even be a factor either due to the small overall span. A beam only takes half the span. the other half is supported on the exterior walls. You can definetly get away with creating a "flitch plate" beam and eliminate the column all together. A flitch plate is the combination of conventional wooden lumber and steel plate sandwiched and thru bolted together. The splice joists overlap creating a solid beam mass. PM me ALL the dimensions of the garage including the overall span of the beam and clg joists above and the directions of each. I'll run a calculation and provide you with what size steel plate and how many additional 2x10 joists you'll need.
I have an architectural degree and its my day job if it helps reassure you... LOL. |
Now that's what this site is all about!!
EEEEEEEEEEEHHHHHHHHAAAAAAAAAAAAA |
Quote:
|
Thanks guys. The beer cans have been in there for probably 12 years or longer. We've never gotten around to cleaning out the attic.
War....when I said adding 2x4's, I meant adding them in a way like a collar tie. Just wasn't sure what they were called. HRBS...thanks a lot. I'll get those measurements but likely won't be until early next week now as go back to work tomorrow and am not off until Tuesday morning. |
Quote:
It looks like you are running 2x4 rafters at 16" o.c. with a 2x6 ridge. Its hard to tell much from the photos about the ceiling joists. Can you provide more detail about the ceiling joist. If the inside of garage picture is any indication that those are the ceiling joist I wouldn't plan on storing anything but aluminum cans up there. I've been building homes since 1988 and have an engineer just a phone call away. If you get me photo, size, and span of garage door header along with the span of the double 2x10 I will give my engineer a call. |
Like I said... I do this all day.
Ridge beams are NOT structural in ANY way. All they do is provide a mounting point for the top of the rafters to meet. The post down to the beam is ONLY there for temporary support (to hold the ridge in place) while being constructed. You as a home builder should know this. You may build homes but you build them to the way people like me design them. Not putting you down in anyway so dont take it that way..... its just that I've seen too many people make mistakes from listening to a builder rather than an architect or engineer. You have an engineer "a phone call away". I dont because I am my own engineer. Thats a BIG difference. But what do I know..... I've only been an Architectural Project Manager for 15 years.... |
I think that I just learned a couple of things... Cool!
|
Quote:
I'm pretty sure when you are done designing a house you are handing the plans over to a structural engineer just like every other architect does. I also have 11 more years experience than you do. Yes, your right, there are a lot of moron contractors out there that dont know what the hell they are doing, but I make no changes to anything structural without my engineers stamped and signed approval. And 90% of the time I already know what he is going to tell me just by going off the shear table and structural pages on the plans. And by the way, my architect did not design my 5000 sf home, my wife and I did. |
Im no engineer or architect, but I did stay at a Holiday Inn Express last night. I say remove the beam and see what happens......just kidding, dont do that! :willy:
I dont know about everyone else, but I'm going to sit back, grill some burgers and watch this. Hopefully there will be some agreement and you can get some direction on what to do. Good luck! |
Gaetano.... seriously I wasnt putting you down and agree I dont want this to be a pissing match. I too many times over have dealt with contractors who took the liberty to make a field change base on something they did on a past job weeks, months sometimes years ago. Just because a situation is similar it couldnt be any further from the same. Each member or beam or header etc is ALWAYS calculated on its particular criteria. there is no "book" or standard. With that said Idont want to frey away from Mikes original post.
Ridge beams are nothing more than a closer for the rafters to nail to PERIOD. Attached are some pics of ridge beams.... please note none of them are supported from underneath like a post would be. They are all simply nailed temporarily to hold them in place untill all the rafters are secured. In the last pic you can also see at the top where the two piece ridge is spliced by a simple 2x4. I am sorry to let you down but you are 100% wrong on this. The ridge size is soley determined on the length (span) of the ridge itself and also by the rafter size and slope (the ridge wants to be larger than the cut angle of the rafter). Another example would be a truss roof. The trusses have no "ridge" they are butted together. Even when they are erected, there is no ridge beam. http://crodog.org/garage/firstrafters.jpg http://crodog.org/garage/ridge2.jpg http://crodog.org/garage/ridge3.jpg http://crodog.org/garage/tempfloor.jpg |
Quote:
Anyway.... great banter... I just hope it isnt taken out of context. I want to add one last time that I am not putting you down. If you knew me personally you would know I dont do that or attempt to call people out. I am just trying to clarify right from wrong and not stating an opinion. |
So back to Mikes OP...
Forget the ridge beam - which everyone knows is just a nailer. Can he truss the roof - or just add collar ties? Is the beam and post he wants to remove - something that was added for support of the "attic" area http://www.rooftrussdesigns.com/RoofFrame.jpg |
LOL Greg...
Yes he can truss the roof but this would be the most expensive ($$) option. The least expensive IMO would be to create a flitch plate beam using the existing 2x10 beam thats there. Basically just add the 1/2" thick steel plates and additional members as calculated. I believe the end post lands in between the 2 garage doors and not over the header that would be on say 1 large garage door. If this is true he would have to open up both end walls and add a 2x4 to each side of what should be a double 2x4 post there already. then he would have to temp. support the clg joists and build the flitch plate beam. Lastly he can then remove the center post in question once completed. This again IMO would be the easiest and least expensive option. |
Quote:
|
You can lead a horse to water........................
Obviously you are not seeing the difference between ridge boards and ridge beams. The photos you posted are ridge boards not beams. I'm done here, nap time, LOL |
Here ya go Mike --- a flitch beam....
http://www.betterheader.com/ Just don't trying saying it fast three times to your wife ... |
:lol: thanks Greg. Well I'll admit, I didn't expect this when I posted that question. In the end, if it's going to be too much of a pain or too much money, I won't do it and will get used to working around it as I'm doing now. I know that posting pics don't always tell the whole store. Before I do anything, I plan on having someone come and look at it and see it in person. I posted this to see if it was even an option. Thanks again to everyone that responded.
|
For what its worth....I had a similar wood post in my shop and chaged it out to an adjustible steel post found in basements. Its cheap like $65 and it is way slimmer and sleeker than the thick wood post. It made a world of differance and was done in a half hour with the metal posts spray painted to match the shop.
|
You two (not mike) need to start another thread on structural analysis for construction. Its not an issue of your degrees and background, its resolving the OPs issue only.
|
Quote:
best post in this whole thread! |
Quote:
|
Mike........... So??????????????????
Are you "postless" yet?? :rofl: :rofl: |
No. I'm not going to worry about it right now. I ended up getting some wheel dollies for my car instead. It rolls around quite easy now with the dollies so easier to work on. I'd still like to eventually remove the post, but haven't gotten around to looking into it more.
|
LOL ---- good!
Car parts or posts.... I'd choose car parts! :cheers: :woot: |
Quote:
|
Oh sorry.. i need to post evidence and sources to back things up.. let me Google.
http://www.structural101.com/Structural-Ridge-Beam.html Supports our theory.. |
The hell with the ridge beam and board and nailer...
Just "hot rod" the existing post the way I did mine! :rofl: :rofl: http://i919.photobucket.com/albums/a...x/DSC_2166.jpg AND YES -- IT IS BOLTED TO THE FLOOR -- but the post is sitting over the bolt so it's blind. And NO I don't give a damn if it's code or not. http://i919.photobucket.com/albums/a...x/DSC_2165.jpg http://i919.photobucket.com/albums/a...x/DSC_2692.jpg A plasma cutter -- and a Burr King.... can make almost anything! |
Thats awesome looking! How or where did you get the flames? that design would be cool on a door kick plate or something aswell :) Ideas ideas..
|
Quote:
In "sheds" like ours (personal toy sheds) stuff like this is not only fun to make -- it's what sets the tone and feel of the dump. :rofl: |
One part of my shop is 32X40 w/ W22X14 inch beam running the 40ft long w/ a 3.5x3.5x1/4 wall sq. tube. as a centered column.There is a second floor of 32x40 above for storeage. which has roughly 60#lbs. per sq. ft.load bearing wt. The engineer I hired when I built the shop said to build the shop w/o the centered column I would need a W42x24 inch beam. ( W42 means 42 pounds per running foot. 24 means 24 inches tall. you will need something of this size to carry that type of load. The engineer charge me $300.00 to size my beam after he looked over my floor plan drawing. Some large steel fabricating frims have engineers on staff that can do the math for you. Good luck.Scott.
|