Your compessor is 16 amps,as far as code goes you can use a 20 amp 2 pole breaker. Max amps is 80% of your breaker size. 16 amps for a 20 amp breaker. you can install a receptacle rated for 20 amps and unplug it for servicing. 10-2 romex will work as long as it isn't subject to physical damage and you tape the white wire black. Per NEC code it should not be run on the surface of the wall without protection, EMT or PVC conduit.
Kevin