Default Home electrical help (welder)

Calling all electricans, EE, people with 220 welders, or whoever wants to give their input. I just bought a lincoln 175 welder, It runs off of 220. Well here is my question the plug in the garage is 220/30amp, but the lincoln recommends that I have 40amp breaker. Is this just a "recommendation" from lincoln or is it manditory that I have a 40amp?
Reply With Quote
  #2  
Old 02-02-2008, 09:35 AM
Beach Cruiser's Avatar
Beach Cruiser Beach Cruiser is offline
Senior Member
 
Join Date: Mar 2006
Location: Virginia Beach, Va
Posts: 603
Thanks: 0
Thanked 1 Time in 1 Post
Default

The worst thing that can happen with an undersized breaker is that it will Trip more often if you over load it. If you find that it trips too frequently then you will need to upgrade to the 40 amp, but you will also need to upgrade the wiring to handle the additional load. If you are just doing light fabrication work and not really taxing the system, the 30 amp breaker should be fine.
__________________
No Shop, No Money, No Time.... No problem!
Reply With Quote
  #3  
Old 02-02-2008, 12:32 PM
awr68's Avatar
awr68 awr68 is offline
Senior Member
 
Join Date: Dec 2004
Location: Oregon
Posts: 6,478
Thanks: 0
Thanked 3 Times in 3 Posts
Default

I thought the 30 and 40 amp plugs are differant....Will your welder even plug into the existing outlet?

Where's Mike?!
__________________
Tony
'68 Camaro
Reply With Quote
  #4  
Old 02-02-2008, 03:54 PM
01somta 01somta is offline
Senior Member
 
Join Date: Jun 2007
Posts: 174
Thanks: 0
Thanked 0 Times in 0 Posts
Default

Quote:
Originally Posted by awr68
I thought the 30 and 40 amp plugs are differant....Will your welder even plug into the existing outlet?

Where's Mike?!
yes they are different, but I made a 10ft ext cord with a 10ga. wire with the correct female plug for the welder and the correct male plug for the wall.
Reply With Quote
  #5  
Old 02-02-2008, 08:46 PM
Bill Howell Bill Howell is offline
Site Sponsor
 
Join Date: Jun 2005
Location: Pigeon Forge, Tn.
Posts: 967
Thanks: 0
Thanked 0 Times in 0 Posts
Default

The problem is the wire from the panel to the plug. I am sure if it was wired for a 30 amp, then the wire was sized accordingly. Be sure to check and see what wire was used before you just switch the breaker. If in fact, proper wire was used (and this will depend on distance from panel to plug as well), then just change the breaker. If not, I suggest you run proper wire and make a new circuit.
__________________
Bill Howell
www.americanstreetcarseries.com
Reply With Quote
  #6  
Old 02-03-2008, 01:36 PM
Bodies67's Avatar
Bodies67 Bodies67 is offline
Junior Member
 
Join Date: Sep 2007
Location: Many, Louisiana
Posts: 16
Thanks: 0
Thanked 0 Times in 0 Posts
Default wire size

I'm a electrical contractor in louisiana. If you have a 30 amp plugin in your wall you should have a # 10 wire for it. If you need a 40 amp plugin on your welder you need a #8 wire to carry that.If you just change the end the welder could pull more amp's than the wire is rated for and either melt the end of the plug or melt the wire in the wall and cause a fire.If you are not going to use it alot you might be OK.But any new or remodel we do and they want a welder plug . We run #6. It 's good for 60 amps. We always over kill but we don't have fires. Hope this was helpful.
Reply With Quote
  #7  
Old 02-03-2008, 06:30 PM
mazspeed's Avatar
mazspeed mazspeed is offline
Senior Member
 
Join Date: Jul 2005
Location: Campbell Ca
Posts: 2,005
Thanks: 0
Thanked 0 Times in 0 Posts
Default

Quote:
Originally Posted by Bodies67
I'm a electrical contractor in louisiana. If you have a 30 amp plugin in your wall you should have a # 10 wire for it. If you need a 40 amp plugin on your welder you need a #8 wire to carry that.If you just change the end the welder could pull more amp's than the wire is rated for and either melt the end of the plug or melt the wire in the wall and cause a fire.If you are not going to use it alot you might be OK.But any new or remodel we do and they want a welder plug . We run #6. It 's good for 60 amps. We always over kill but we don't have fires. Hope this was helpful.

Great advice here. I tend to run upsize the wire for welders and certain machines due to the fact that they will run a bit hotter as well. Less voltage drop. 30 amp will more then likely have #10 wire which is too small for a 40 amp welder. #8 is fine, but you need at least #8.
Reply With Quote
  #8  
Old 02-04-2008, 04:59 AM
Tiger's Avatar
Tiger Tiger is offline
Senior Member
 
Join Date: Dec 2007
Location: Italy
Posts: 125
Thanks: 0
Thanked 0 Times in 0 Posts
Default ??

Hi,
I'm curious because I have the same welder and can run it all day at full power out of my 220v/16A (I'm in Europe) outlet without ever triggering the breaker.
Could it be that there is some kind of conversion from 110/220 (like that the breakers are on the 110v side before converting to 220V or something like that)?
because if you are talking about 30/40A on 220volts that is allot
It is 6,6kw for 30A and 8,8kw for a 40A.
__________________
André

2009 Chrysler 300C Touring.
3.0 liter V6 diesel, five speed auto.

1968 Chevelle Coupe.
355cid, Viper T56, Corvette C4 IRS (Dana 44) and C4 IFS. Porsche 6 and 4 piston Brembo's.

1980 Chevy Van (shortie G10).
355cid, TH350, 8.5" 10bolt posi and Belltech spindles.

*NOW PARTING OUT* 2000 BMW 540i Wagon*

Bikes
1968 Benelli City Bike
1990 Yamaha RD 350
1990 Yamaha TZR 125R
1991 Yamaha TZR 125R - RD350 engine, Aprilia RSV forks, RS250 wheels and shock
2010 Buell XB12SS
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 07:26 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2025, vBulletin Solutions Inc.
Copyright Lateral-g.net